Hope someone can help… The issues I’m have are hard to explain… I have 4 12v 100a bluetooth/heated SOK’s hooked to a Victron Multiplus ll. When on shore power they all read 100% and the CMOS is gray and everything works fine. If I unplug from shore power - and continue to run the A/C in my Motorhome on solar/battery, the Multiplus shuts down the AC power and the ‘low battery’ and ‘overload’ red lights on the Multiplus come on. The SOK-BMS app shows BOTH the CMOS and the DMOS have switched to gray and only the DC power works in the Motorhome. Then, if I plug back into shore power, eventually the CMOS and DMOS go to green. Is this an issue with my SOK batteries or with the Victron Multiplus? Any solution/suggestions are welcome. TIA, Craig.
top of page
To see this working, head to your live site.
Problems with SOK 12v 100a batteries CMOS and DMOS???
Problems with SOK 12v 100a batteries CMOS and DMOS???
2 answers0 replies
Like
2 Comments
bottom of page
I am seeing a similar problem.
- 2 SOK 100-Heated in parallel
- A BMV 712 battery monitor
- A 12V, 2K Multiplus.
If the Current as read by the BMV712 gets much above 100A, the batteries shut down. (With 2 in parallel, I should be able to draw 200A)
When I put a load on that draws about 80A as read by the BMV712, the BMS in each battery reports 75A (for a total of 150A). This tells me the current sensor in the BMS is off by nearly a factor of 2!!
Check this:
https://www.us.sokbattery.com/forum/questions-answers/how-to-read-and-set-the-abc-bms-app